Minimum Voltage at incoming supply point

Retired now and not up to date with reg’s since 16th. Helping advise a friend. Currently they have 100amp single phase supply and whilst the no load voltage is up at around 238 volts, as the circuit is loaded, voltage drops off substantially. Even with a load of 50 amps, ie, half the supply fuse rating, voltage is slightly below the -6% limit, at around 215 volts, further load simply pushes voltage significantly lower, and by extrapolating measured data, it would be nearer 170 volts with a load of 100 amps, is this acceptable? I plan measuring Ze and pfc this week as a guide perhaps to supply loop impedance and, which I suspect must be causing this excessive drop. I’m aware of the ESQCR reg’s although need to update myself, but are there any other regulations that apply?

Parents
  • Believe what you want UKPN, the response I’ve seen from the DNO is pathetic (I’ve only just taken up the case), and I have done the measurements, calculations and submitted a detailed report, and await the outcome. Have worked for the CEGB -power stations- that was a while ago!), and most recently, as a Council Electrical Contracts Engineer (a hobby during retirement), and even surveyed total plant and services for major NHS hospitals (some of them are in a mess!), and much more. Including as a drives engineer and controls specialist over a long career in the industry. I am very use to having to do such investigations, but not up to date with latest Reg’s (several years into retirement), hence the question on here, and appreciated the answers. Now sitting on it awaiting DNO response. Back in 2006, after initial early retirement, I also completed the C&G2391, not because I needed it, but because it looked interesting, and found in practice that some of it could be nearly as difficult as earlier degree and HNC’s exams, and back then, most failed it, but I think they have simplified it since.

Reply
  • Believe what you want UKPN, the response I’ve seen from the DNO is pathetic (I’ve only just taken up the case), and I have done the measurements, calculations and submitted a detailed report, and await the outcome. Have worked for the CEGB -power stations- that was a while ago!), and most recently, as a Council Electrical Contracts Engineer (a hobby during retirement), and even surveyed total plant and services for major NHS hospitals (some of them are in a mess!), and much more. Including as a drives engineer and controls specialist over a long career in the industry. I am very use to having to do such investigations, but not up to date with latest Reg’s (several years into retirement), hence the question on here, and appreciated the answers. Now sitting on it awaiting DNO response. Back in 2006, after initial early retirement, I also completed the C&G2391, not because I needed it, but because it looked interesting, and found in practice that some of it could be nearly as difficult as earlier degree and HNC’s exams, and back then, most failed it, but I think they have simplified it since.

Children
No Data