Minimum Voltage at incoming supply point

Retired now and not up to date with reg’s since 16th. Helping advise a friend. Currently they have 100amp single phase supply and whilst the no load voltage is up at around 238 volts, as the circuit is loaded, voltage drops off substantially. Even with a load of 50 amps, ie, half the supply fuse rating, voltage is slightly below the -6% limit, at around 215 volts, further load simply pushes voltage significantly lower, and by extrapolating measured data, it would be nearer 170 volts with a load of 100 amps, is this acceptable? I plan measuring Ze and pfc this week as a guide perhaps to supply loop impedance and, which I suspect must be causing this excessive drop. I’m aware of the ESQCR reg’s although need to update myself, but are there any other regulations that apply?

Parents
  • Former Community Member
    0 Former Community Member
    So we've gone from considering to actually having them installed without getting the supply upgraded then. As before, it appears the cost of getting the supply upgraded was deemed unnecessary so the install went ahead and now the reasons for a paid for increase in ASC have come home to roost.......

     The situation, which started with a request for a 3-phase supply very much earlier this year, when pool heat pumps were being considered,

    For the installation I’m looking at (for a friend, so just out of interest in my retirement), the current demand, by domestic standards is large, and includes heat-pumps for both house and pool, and these in particular are being adversely affected by the low voltage. There are implications too re the COP of heat pumps and lots more with at these low voltages, so I have just submitted a comprehensive technical report to the DNO and asked for an urgent response.


    Regards


    BOD


Reply
  • Former Community Member
    0 Former Community Member
    So we've gone from considering to actually having them installed without getting the supply upgraded then. As before, it appears the cost of getting the supply upgraded was deemed unnecessary so the install went ahead and now the reasons for a paid for increase in ASC have come home to roost.......

     The situation, which started with a request for a 3-phase supply very much earlier this year, when pool heat pumps were being considered,

    For the installation I’m looking at (for a friend, so just out of interest in my retirement), the current demand, by domestic standards is large, and includes heat-pumps for both house and pool, and these in particular are being adversely affected by the low voltage. There are implications too re the COP of heat pumps and lots more with at these low voltages, so I have just submitted a comprehensive technical report to the DNO and asked for an urgent response.


    Regards


    BOD