This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Minimum Voltage at incoming supply point

Retired now and not up to date with reg’s since 16th. Helping advise a friend. Currently they have 100amp single phase supply and whilst the no load voltage is up at around 238 volts, as the circuit is loaded, voltage drops off substantially. Even with a load of 50 amps, ie, half the supply fuse rating, voltage is slightly below the -6% limit, at around 215 volts, further load simply pushes voltage significantly lower, and by extrapolating measured data, it would be nearer 170 volts with a load of 100 amps, is this acceptable? I plan measuring Ze and pfc this week as a guide perhaps to supply loop impedance and, which I suspect must be causing this excessive drop. I’m aware of the ESQCR reg’s although need to update myself, but are there any other regulations that apply?

Parents
  • Yes, great in the summer Andy, but not so good this time of year, I regularly watch the gridwatch site (currently showing zero for solar of course). and fitted daughters canal boat out with them, great in the summer, but she is back to generator/engine again for the winter of course.
Reply
  • Yes, great in the summer Andy, but not so good this time of year, I regularly watch the gridwatch site (currently showing zero for solar of course). and fitted daughters canal boat out with them, great in the summer, but she is back to generator/engine again for the winter of course.
Children
No Data