Earth Leakage - Boiler?

Called at my friend's house where he is looking to run CAT6 underground today and he was telling me about his RCD tripping problem.


Virtually every day his RCD trips. Single phase overhead TT supply. Single 30mA RCD in Consumer Unit.

The problem started soon after a new oil fired CH boiler was fitted.

Putting a clamp meter around the meter tails, from 21 to 0mA unbalance step by step as the single pole MCBs were opened one by one.

Rather upsetting to find that with all MCBs in and 21mA unbalance there was only 2mA in the earth lead, could not find either the cable connection or the rod outside.

Hoping to find a convenient place on the boiler where I could access the L & N to check unbalance looked inside and nothing accessible within the time I had. Anyway out of "devilment" you could say, put the clamp meter around one of the CH pipes from the boiler and 21 mA flowing through the 22mm pipe! I'm guessing that assuming the cable and rod are ok, the earth leakage current will flow inversely proportional to the respective resistances.

He has been trying to get an Electrician in to sort out.

Besides ensuring a decent earth rod and cable to the MET I think the ideal would be a new Consumer Unit (metal of course) and Cobs.

To try and confirm the boiler being the main cause, since the CH system runs from a nearby 13a socket, have considered a short extension lead where the L, N & E are separated out for easy application of a clamp meter.

Any other checks to try before his Electrician gets in heavy style?


Clive



Parents
  • Clive,

    your thoughts look sensible to me.

    Just one small mention ref RCD being oversensitive - in my (limited) experience RCDs usually work as per spec or not at all or are sluggish. I have not yet found any that are over sensitive per se. When one appears over sensitive it is often the standing leakage from other circuits/equipment that is causing this. Example, say you already have 11mA leakage and then you introduce a couple of items/circuits with 5mA each you are well within the permissible tripping zone of an RCD. Of course others may have actually found over sensitive RCDs when tested with no circuits connected - I`d love to hear of it.


    It`s also good to hear about different disciplines too. Mine is mostly domestic with a bit of commercial, yours is on board ships. People often expect me to know all about car electrics, well I do know a bit but an experienced auto electrician would run rings around me with fault finding (I am aware that poor chasis connections can cause strange happenings though)  but I`d probably trump them with a house electrics.
Reply
  • Clive,

    your thoughts look sensible to me.

    Just one small mention ref RCD being oversensitive - in my (limited) experience RCDs usually work as per spec or not at all or are sluggish. I have not yet found any that are over sensitive per se. When one appears over sensitive it is often the standing leakage from other circuits/equipment that is causing this. Example, say you already have 11mA leakage and then you introduce a couple of items/circuits with 5mA each you are well within the permissible tripping zone of an RCD. Of course others may have actually found over sensitive RCDs when tested with no circuits connected - I`d love to hear of it.


    It`s also good to hear about different disciplines too. Mine is mostly domestic with a bit of commercial, yours is on board ships. People often expect me to know all about car electrics, well I do know a bit but an experienced auto electrician would run rings around me with fault finding (I am aware that poor chasis connections can cause strange happenings though)  but I`d probably trump them with a house electrics.