Electrical Regs in Ireland (Dublin)

Are there any Regs or conventions restricting the amount of sockets per circuit in Dublin?


Having just done Berlin, it seems that each circuit did one socket, and I rightly, or wrongly, added one socket in a radial fashion using BS8436.


I'm about to add to existing circuits again in Dublin and wondered if anyone had a copy of the irish regs or knew from experience?


Kind Regards


Tatty
Parents
  • ET101 suggests a maximum of 10 points across no more than two rooms (excluding hallways) for a radial socket circuit (with an unlimited number for a ring final circuit).


    You should be familiar with acceptable cable types etc. and the requirement for certification should any Controlled Works be carried out.
Reply
  • ET101 suggests a maximum of 10 points across no more than two rooms (excluding hallways) for a radial socket circuit (with an unlimited number for a ring final circuit).


    You should be familiar with acceptable cable types etc. and the requirement for certification should any Controlled Works be carried out.