OSG 7.3.2 cables in walls and partitions

In the above,item d states the cables can be protected by earthed steel conduit or,

Item e then states :mechanical protection sufficient to prevent penetration of nails,etc,

but no mention of earthing..

I have a situation with a short 200mm horizontal run outside the zones.

I could slide a lenght of earthed conduit over,but then the earth connection would be plastered

over and could not be inspected.

If I treat the conduit as mechanical protection,it would not need earthing?

Wondered what others would do.

                                                        Regards,Hz

Parents
  • Former Community Member
    0 Former Community Member

    Chris Pearson:

    But I think that this is a different situation. I reckon about 1/4" of steel plate would do the trick.



     



    Should be good for a standard NATO round  - need a bit more for 7.62 x 51 AP ?


    OMS
     

Reply
  • Former Community Member
    0 Former Community Member

    Chris Pearson:

    But I think that this is a different situation. I reckon about 1/4" of steel plate would do the trick.



     



    Should be good for a standard NATO round  - need a bit more for 7.62 x 51 AP ?


    OMS
     