AJJewsbury:
For example, from Eland:
Protective devices used for these cables shall be either Type B to BS EN 60898 or Type B RCBO to BS EN 61009-1. The protective devices shall have a maximum let through energy (l2t) of 42000A2s when used with 1.0mm2 or 1.5mm2 cable and 60000 A2s when used with 2.5mm2 or 4.0mm2 cable.
Whereas the k²S² for a 1mm² c.p.c. (as in 1.0mm² and 1.5mm² T&E) would be just 13,225A²s and a a 1.5mm² c.p.c. (as in 2.5mm² and 4mm² T&E) would be just 29,756.25A²s.
AJJewsbury: