Presumably it has been tested for occasions where a nail may just penetrate the aluminium covering part and touch the phase conductor as well. Or is the cable only compliant for burying out of zones if the C.P.C. is also touched by the invading nail?
Flexishield has been specifically developed for applications where cables are required to be concealed within partitions and building voids, at a depth of less than 50mm.
Flexishield’s main feature is it’s ability to fail safe when used as part of an electrical circuit that is penetrated by a sharp metallic object. The cable has now been designed to fail safe at 200 amps under nail penetration conditions, as such it will operate an MCB of up to 40A Type B or up to 20A Type C this surpassing the requirements of BS8436. A fully compliant cable, Flexishield is a cost effective solution to meet the 18th Edition of The Wiring Regulations BS 7671:2018 for concealed cables at a depth of less than 50mm, Regulations 522.6.201 to 522.6.204.
Flexishield is a protected fixed wiring cable, it uses a bonded aluminium tape which gives excellent mechanical resistance and acts as an effective screen to help reduce electrical interference. Flexishield has been independently certified to BS 8436 (300/500v) and IS 273 (600/1000v) by BASEC.
Flexishield as standard comes in the range of 1.5 to 4.0mm2 to BS 8436 300/500v and the 6.0mm2 to IS 273 600/1000v. All available with stranded conductors of 2, 3 and 4 cores and a CPC of equal cross sectional area. Standard sheath colour is white, core colours as per the harmonised wiring codes and supplied on 100m drums. Options by request are available with sheath and core colours, drum lengths and 600/1000v ratings on the 1.5 to 4.0mm2 sizes.
So do we just connect the C.P.C. to an earth terminal as usual? Or do we have to gland the cylindrical foil in any special way?
24 April 2015 08:50 AM ![]() |
AJJewsbury Posts: 17795 Joined: 13 August 2003 |
| If the cable was being used for its screening purposes rather than its ADS foil screen nail penetration charateristics, could it be used with type C devices, as the nail test is irrelevant in this case? It would be no worse than FP200 type cables that can be used with 'C's, and whose screen is inferior to the 8436 standard?? Makes sense to me. BS8436 is limited to type B devices That always felt like a bit of an oversimplification to me - if a B32 is OK, then why not a C16 for instance? - the maximum permitted energy let-through is the same. Or even a fuse if the conditions are right. - Andy. |