AJJewsbury:
I don't recall any regulation specifically demanding an all-insuated fuse box (although it might have passed me by). It might have been implied by more general regulations though - e.g. the need to provide shock protection, ADS not being practical in some situations (say with high Ze) so obliging a double/reinforced insulation approach for TT systems and similar.
There's been a reminder of that in the regs for a while - e.g. 531.4.1 in the 17th - which became 531.3.5.3.2.201 in the 18th - but neither really demand an all-insulated approach - as it has always been possible to have a double/reinforced insulation system within metal enclosures.
- Andy.
AJJewsbury:
I don't recall any regulation specifically demanding an all-insuated fuse box (although it might have passed me by). It might have been implied by more general regulations though - e.g. the need to provide shock protection, ADS not being practical in some situations (say with high Ze) so obliging a double/reinforced insulation approach for TT systems and similar.