Why RCD is unallowed in TNC system? I think it is useful for preventing indirect electric shock

Former Community Member
Former Community Member
Why RCD is unallowed in TNC system? I think it is useful for preventing indirect electric shock. For example when a fault happens (phase to metal body) and a person contacts the metal body, current flows from his body and goes to the earth. So Unbalancing current of phase and PEN inside of RCD make it to be triped.
  • In a TNC system (unlike a TN-S or TNC-s) you cannot tell what is a legitimate neutral current, and what is an earth fault current using the PEN, as the earth and neutral path is common.

    Therefore there will be multiple connections from the PEN to parallel paths (imagine TNC distribution and metal water pipes feeding a row of buildings - at each building the water pipe is earthed by a water heater.) so the neutral current is expected to follow these alternate paths   to some degree, so the live and PEN current are not in balance, even when all is working well.

    If however you were very careful to only connected the PEN to earth at one point, then what you say would work, but the second connection to earth - the person, would unbalance the system.
  • I am not allowed to install a TNC system in the UK.


    A RCD cannot work on a TNC system until the earth is separated, which is how it is done elsewhere in the world.


    Andy Betteridge
  • Former Community Member
    0 Former Community Member

    mapj1:

    In a TNC system (unlike a TN-S or TNC-s) you cannot tell what is a legitimate neutral current, and what is an earth fault current using the PEN, as the earth and neutral path is common.

    Therefore there will be multiple connections from the PEN to parallel paths (imagine TNC distribution and metal water pipes feeding a row of buildings - at each building the water pipe is earthed by a water heater.) so the neutral current is expected to follow these alternate paths   to some degree, so the live and PEN current are not in balance, even when all is working well.

    If however you were very careful to only connected the PEN to earth at one point, then what you say would work, but the second connection to earth - the person, would unbalance the system.




    So many thanks. Do you mean in TNC system, There is unwanted tripping of RCD so because of this we can not use RCD?

  • Former Community Member
    0 Former Community Member
    So many thanks. Do you mean in TNC system, There is unwanted tripping of RCD so because of this we can not use RCD?


    How many conductors are there on the consumer's side of the supply and of these two (whoops, gave the clue away) what are their functions?


    Next, how does an RCD work?


    Regards


    BOD

  • Do you mean in TNC system, There is unwanted tripping of RCD so because of this we can not use RCD?




    yes -

    In a TNC circuit with a singly earthed PEN, it will quite correctly only trip on faults to terra-firm earth, and not trip on faults to PEN (as these are the same as legitimate currents L-N)


    In a TNC system with a PEN earthed in more than one place ( for example the distribution side of a PME or MEN  installation) then PEN and live currents are always out of balance, so any RCD will operate, even if there is no fault . This is why when there is a power cut and the DNO bring in a hired genset to back feed the network, their first act is to disable the earth leakage trip


    This may or may not be unwanted.