The maximum permissible disconnection time is 0.4 s in TN system. Why and from where this value (0.4 s) is obtained?

Former Community Member
Former Community Member
The maximum permissible disconnection time in in the event of a short circuit between a phase conductor and a body or protective conductor or a protective-neutral conductor is 0.4 s in TN system. Does anybody know this value (0.4 s) obtains from where? How this value is obtained?
Parents

  • Where did you get that colour graph if it is not a rude question as the one in 60479 is B&W



    Google found it here for me: https://commons.wikimedia.org/wiki/File:IEC_TS_60479-1_electric_shock_graph.svg

     

    What about the 5s disconnection time where did that come from?



    The legend I heard was that it dated from (smoke filled rooms) when the regs committee first started discussing disconnection times and one member did a quick back of an envelope calculation based on what he knew about the circuits where he worked in his normal day job - and reckoned that they'd have to permit up to 5s if his system was going to continue to comply.


    There's probably a co-incidenal relationship between most fuse characteristics and an acceptable voltage drop - which usually means that if the voltage drop is acceptable the loop impedance will be such that disconnection time will probably happen within about 5s too.


       - Andy.
Reply

  • Where did you get that colour graph if it is not a rude question as the one in 60479 is B&W



    Google found it here for me: https://commons.wikimedia.org/wiki/File:IEC_TS_60479-1_electric_shock_graph.svg

     

    What about the 5s disconnection time where did that come from?



    The legend I heard was that it dated from (smoke filled rooms) when the regs committee first started discussing disconnection times and one member did a quick back of an envelope calculation based on what he knew about the circuits where he worked in his normal day job - and reckoned that they'd have to permit up to 5s if his system was going to continue to comply.


    There's probably a co-incidenal relationship between most fuse characteristics and an acceptable voltage drop - which usually means that if the voltage drop is acceptable the loop impedance will be such that disconnection time will probably happen within about 5s too.


       - Andy.