The maximum permissible disconnection time is 0.4 s in TN system. Why and from where this value (0.4 s) is obtained?

Former Community Member
Former Community Member
The maximum permissible disconnection time in in the event of a short circuit between a phase conductor and a body or protective conductor or a protective-neutral conductor is 0.4 s in TN system. Does anybody know this value (0.4 s) obtains from where? How this value is obtained?
Parents

  • Presumably distribution circuits are allowed to have long disconnect times because they don't expect anyone to actually come into live contact with them very often (apart from the occasional shortly-to-be-deceased sparky fiddling about inside a DB). All the nasty end-user paraphernalia like water heaters, power tools etc are connected further downstream with 0.2/0.4s disconnect times.



    Unfortunately the situation isn't quite that good. If there's a fault on a submain, the earth bar on the DB it serves - together with all the downstream exposed-conductive-parts - will likely be held at the fault voltage (e.g. 115V for TN, 230V for TT) until disconnection occurs (e.g. for the full 5s) - so you can still get a 5s shock from metalwork on a 0.4s circuit.


    I suspect the allowance for 5s disconnection is more to do with the practicalities of achieving discrimination (possibly through several stages of sub-mains) and being able to use a range of overcurrent devices (e.g. fuses) within practical loop impedances, together with the lower likelihood of faults on submains etc - rather than any comprehenive plan for shock protection.


    In theory main bonding can help a bit - but in practice the benefit isn't anything like sufficient to be guaranteed to be life-saving.


       - Andy.
Reply

  • Presumably distribution circuits are allowed to have long disconnect times because they don't expect anyone to actually come into live contact with them very often (apart from the occasional shortly-to-be-deceased sparky fiddling about inside a DB). All the nasty end-user paraphernalia like water heaters, power tools etc are connected further downstream with 0.2/0.4s disconnect times.



    Unfortunately the situation isn't quite that good. If there's a fault on a submain, the earth bar on the DB it serves - together with all the downstream exposed-conductive-parts - will likely be held at the fault voltage (e.g. 115V for TN, 230V for TT) until disconnection occurs (e.g. for the full 5s) - so you can still get a 5s shock from metalwork on a 0.4s circuit.


    I suspect the allowance for 5s disconnection is more to do with the practicalities of achieving discrimination (possibly through several stages of sub-mains) and being able to use a range of overcurrent devices (e.g. fuses) within practical loop impedances, together with the lower likelihood of faults on submains etc - rather than any comprehenive plan for shock protection.


    In theory main bonding can help a bit - but in practice the benefit isn't anything like sufficient to be guaranteed to be life-saving.


       - Andy.