I came across an issue with the Inspection schedule for an EICR last week. When a measured value of PFC is higher than the protective device KA value installed within the Distribution board, I would flag a C2 observation (I think the classification of the observation is a different post....). I would add this to the C2 to the inspection schedule on item 5.7. My issue is the regulation number highlighted after the text for item 5.7. It is 411.3 which is the section for "Requirements for fault protection" I don't feel this really covers the observation.
I came across an issue with the Inspection schedule for an EICR last week. When a measured value of PFC is higher than the protective device KA value installed within the Distribution board, I would flag a C2 observation (I think the classification of the observation is a different post....). I would add this to the C2 to the inspection schedule on item 5.7. My issue is the regulation number highlighted after the text for item 5.7. It is 411.3 which is the section for "Requirements for fault protection" I don't feel this really covers the observation.