lyledunn:
Graham,
do you mind expanding on item 2?
Zoomup:
lyledunn:
Graham,
do you mind expanding on item 2?I think that Graham is implying that any sudden disconnection of the loaded 100m cable, may induce a large Voltage whilst the magnetic field collapses in it, that might damage connected equipment or even the insulation of the cabling. The S.P.D.s would adsorb that high Voltage and limit damage.
Z.
Zoomup:
lyledunn:
Graham,
do you mind expanding on item 2?I think that Graham is implying that any sudden disconnection of the loaded 100m cable, may induce a large Voltage whilst the magnetic field collapses in it, that might damage connected equipment or even the insulation of the cabling. The S.P.D.s would adsorb that high Voltage and limit damage.
Z.
UKPN:
This shed, because of its construction should be protected by an independent earth electrode and rccd. The origin, at the fusebox, PME, protects the cable. The DNO req a min distance of 2 metres from the electrode to PME bonded material. The separate earth lead is a good idea in this case for future use, the cpc of the cable being too small to meet the PME regs.
Regards, UKPN