Sparks79:
Zoomup:
Chris Pearson:
Zoomup:
UKPN:
This shed, because of its construction should be protected by an independent earth electrode and rccd. The origin, at the fusebox, PME, protects the cable. The DNO req a min distance of 2 metres from the electrode to PME bonded material. The separate earth lead is a good idea in this case for future use, the cpc of the cable being too small to meet the PME regs.
Regards, UKPNWhat P.M.E. regs will not be complied with if just the S.W.A. cable armour is used to supply the building, justifying the need for a separate "earth lead". There will be no main bonding to carry out as the incoming water pipe is plastic?
We are told that this shed has a tin roof, and walls. Should they be bonded or not? If they don't actually reach the ground, and the frame is not conducting, it is difficult to see how they are ECPs, so don't bond.
PME earths can be "exported" (even after Brexit ? ) but only provided that the CPC is sufficient to provide main bonding.
If these structures are caravans or tents, then as others have said above, the special locations rules apply.
Incidentally, I wouldn't worry about the extra cost of 3-core as opposed to 2-core, or even the CSA size of the cable - it is small in comparison with the cost of digging the trench, etc. And BTW, it is difficult to terminate 25 mm2 SWA into a 25 mm2 terminal ('cos the core isn't round) let alone a 16 mm2 one!
I think that the O.P refers to the metal parts of the shed being earthed not bonded. Perhaps with its own earth electrode(s). I would not bond the metal external shed parts at all, it is not necessary and could introduce a hazard like main bonding a metal walled caravan.
Are there any extraneous gas pipes in the shed?
Z
Hi Z, currently no extraneous gas pipes, I believe if any gas is introduced it will be from a gas bottle for a gas hob, no pipes in the ground.
Zoomup:
Chris Pearson:
Zoomup:
UKPN:
This shed, because of its construction should be protected by an independent earth electrode and rccd. The origin, at the fusebox, PME, protects the cable. The DNO req a min distance of 2 metres from the electrode to PME bonded material. The separate earth lead is a good idea in this case for future use, the cpc of the cable being too small to meet the PME regs.
Regards, UKPNWhat P.M.E. regs will not be complied with if just the S.W.A. cable armour is used to supply the building, justifying the need for a separate "earth lead". There will be no main bonding to carry out as the incoming water pipe is plastic?
We are told that this shed has a tin roof, and walls. Should they be bonded or not? If they don't actually reach the ground, and the frame is not conducting, it is difficult to see how they are ECPs, so don't bond.
PME earths can be "exported" (even after Brexit ? ) but only provided that the CPC is sufficient to provide main bonding.
If these structures are caravans or tents, then as others have said above, the special locations rules apply.
Incidentally, I wouldn't worry about the extra cost of 3-core as opposed to 2-core, or even the CSA size of the cable - it is small in comparison with the cost of digging the trench, etc. And BTW, it is difficult to terminate 25 mm2 SWA into a 25 mm2 terminal ('cos the core isn't round) let alone a 16 mm2 one!
I think that the O.P refers to the metal parts of the shed being earthed not bonded. Perhaps with its own earth electrode(s). I would not bond the metal external shed parts at all, it is not necessary and could introduce a hazard like main bonding a metal walled caravan.
Are there any extraneous gas pipes in the shed?
Z
whjohnson:
I'm not a TT fan. Too many non-constants.
Bang a rod in. measure once and forget about it - that's the usual norm. No future monitoring, nothing. A 100ma Type S up front? But will it work when needed? How long will a Type B32A mcb sit there with a potentially lethal fault current before it knocks off?
In urban locations it can be nigh on impossible to install, let alone maintain - I've seen too many with the earthing conductor cut off.." because it looks unsightly in the front garden flowerbed and it doesn't really do anything does it?"
Round here there's next to no chance of getting a rod in - solid limestone means that it is often much cheaper to get a PME conversion and transfer liability to the supply company for future maintenance of the earthing facility.
As for exporting PME? I do it via combining the armour and 3rd core to outbuildings at both ends.
Nice low Zs at the destination and job done.
Given the right conditions, I also bang in a rod and combine both earths at a common point just for belt and braces.
Zoomup:
If the S.W.A. is made to B.S. 3646 the armouring of 25mm2 would be a copper equivalent of approx. 26mm2. But, often the S.W.A. cable does not conform to that standard.
https://www.earthingnuts.co.uk/pdf/pvc_xlpe.pdf
And.....https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=47544&enterthread=y&STARTPAGE=2
Z.
(timber frame, metal sheet clad)
or potentially a 2 core SWA with a seperate 10mm CPC (slight cost reduction)
Chris Pearson:
Zoomup:
UKPN:
This shed, because of its construction should be protected by an independent earth electrode and rccd. The origin, at the fusebox, PME, protects the cable. The DNO req a min distance of 2 metres from the electrode to PME bonded material. The separate earth lead is a good idea in this case for future use, the cpc of the cable being too small to meet the PME regs.
Regards, UKPNWhat P.M.E. regs will not be complied with if just the S.W.A. cable armour is used to supply the building, justifying the need for a separate "earth lead". There will be no main bonding to carry out as the incoming water pipe is plastic?
We are told that this shed has a tin roof, and walls. Should they be bonded or not? If they don't actually reach the ground, and the frame is not conducting, it is difficult to see how they are ECPs, so don't bond.
PME earths can be "exported" (even after Brexit ? ) but only provided that the CPC is sufficient to provide main bonding.
If these structures are caravans or tents, then as others have said above, the special locations rules apply.
Incidentally, I wouldn't worry about the extra cost of 3-core as opposed to 2-core, or even the CSA size of the cable - it is small in comparison with the cost of digging the trench, etc. And BTW, it is difficult to terminate 25 mm2 SWA into a 25 mm2 terminal ('cos the core isn't round) let alone a 16 mm2 one!