This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

RCBO's and IR testing

I have had a problem with 5 off Wylex RCBO's. These were bought by a houseowner and fitted by him as there was no RCD protection for some circuits requiring such. These Wylex RCBO's have a warning hidden on the body that connections should be disconnected for Insulation Testing ..........too late the man cried!. For expediency and availability, I have redesigned the arrangement to have MCB's with a common RCBO as a M.S..

I have been in contact with Wylex technical help, who say that they should have been OK to withstand 250V IR testing as in this case, but to return them to the dealer. Anyone else have had similar problems?


Jaymack .
Parents
  • AFDD- Arc Fault Detection Devices are on the list of equipment that cannot be subjected to a 500 volt global insulation tests.


     Andy Betteridge.
Reply
  • AFDD- Arc Fault Detection Devices are on the list of equipment that cannot be subjected to a 500 volt global insulation tests.


     Andy Betteridge.
Children
No Data