RCBO's and IR testing

I have had a problem with 5 off Wylex RCBO's. These were bought by a houseowner and fitted by him as there was no RCD protection for some circuits requiring such. These Wylex RCBO's have a warning hidden on the body that connections should be disconnected for Insulation Testing ..........too late the man cried!. For expediency and availability, I have redesigned the arrangement to have MCB's with a common RCBO as a M.S..

I have been in contact with Wylex technical help, who say that they should have been OK to withstand 250V IR testing as in this case, but to return them to the dealer. Anyone else have had similar problems?


Jaymack .
Parents
  • Which Wylex RCBOs are they?


    The new double pole RCBOs advertised benefits include:


    “Wylex RCBOs go one step further, they have switched neutral built in as standard, live and neutral conductors do not have to be disconnected for insulation resistance testing. This saves time and money, particularly for responsible landlords who regularly test installations during occupancy voids.”

    Electrium
Reply
  • Which Wylex RCBOs are they?


    The new double pole RCBOs advertised benefits include:


    “Wylex RCBOs go one step further, they have switched neutral built in as standard, live and neutral conductors do not have to be disconnected for insulation resistance testing. This saves time and money, particularly for responsible landlords who regularly test installations during occupancy voids.”

    Electrium