Of course it matters what they serve, presumably the connected equipment HAS TO BE protected by a a Type C MCB because it has an inrush current that would trip a Type B MCB.
weirdbeard:
Keith Jones:
I am looking to use it as an alternative to SWA cable base on ease of installation and coat in commercial installations.
Hi Keith have you considered A Hituff style cable?
Sparkingchip:
pww235:
It doesn't really matter what they serve does it?
The key constraints are the required circuit breaker type/rating, the limitation on available conductor sizes and the installation method information available from the manufacturer.
P
Of course it matters what they serve, presumably the connected equipment HAS TO BE protected by a a Type C MCB because it has an inrush current that would trip a Type B MCB.
Or are you applying some unwritten rule that in commercial installations Type C MCBs are used, because that’s the way it’s done?
Also if the cable is in a safe place within the cable tray why does it need any armour or earthed protection at all, unless it needs it when it drops out of the tray to the connected equipment?
I presume this is going to be some cable choice based on the colour of the sheath available rather than what the cable is actually designed for, in which case you drop the spec done to some white sheathed low smoke twin and earth cable, the customer won’t know the difference when they are stood looking up at it.