due to the requirement to limit fault current in the event of the cable being penetrated
Sparkingchip:
Looking at a cable data sheet the answer is no.
Protective devices used for these cables shall be either Type B to BS EN 60898 or Type B RCBO to BS EN 61009-1. The protective devices shall have a maximum let through energy (l2t) of 42000A2s when used with 1.0mm2 or 1.5mm2 cable and 60000 A2s when used with 2.5mm2 or 4.0mm2 cable.
It is not designed for use on cable tray, why are you proposing to use it?
Andy Betteridge
Keith Jones:
Thank you for your replies.
I am looking to use it as an alternative to SWA cable base on ease of installation and coat in commercial installations.
Andy Lewsbury - I understand the concept of I2t/K2S2. And I agree that the restriction to limit the circuit protection to B Type only is an overkill. The cable is to be clipped direct on the walls and supported on cable tray/basket containment with a low risk of penetration.
Sparkingchip - I am looking at the BATT Cable Data sheet for their Guardian XLPEAli tube LSZH Cable and they provode current carrying capacities for Reference 11 (on cabe tray) . I am interested to hear which manufacturers data sheet you are looking at?
I was recently told by a contact on Linkedin that manufacturers have undertaken improvements to the cable and that the B Type requirement had now been relaxed. However, I cannot find evidence of this on any manufacturers website .
Keith Jones:
. . . Batt cables state that their cable can withstand a fault current of up to 200 amp which according to Fig 3A5 BS7671 is the current required to operate a 20 AMP Type C MCB 0.1 TO 5 Seconds. . .