Evnin' all,

                       I have a holiday chalet park with about 80+ chalets on it that I am responsible for electrically. In the main intake room there is a Delta 657 that supplies the Glasgow Excel 200 Amp three phase fused switch. I went to lubricate it today. It has a retracting handle and is very mechanical inside, with a flag that shows ON or OFF through a little window. The red phase fuse seems to be original, as is the yellow phase fuse. The blue phase fuse has been replaced at some point in time and seems newer than the other two. (Busmann DD200.)


Now what I noticed is that the fingers on the blue phase switch blades are damaged and burnt back by a mm or two. It appears that the switch has been opened on a heavy load, or that the contacts are deteriorating due to additional loads being added. Did the old fuse blow due to overheating of the contacts, or are the contacts damaged due to the fuse getting hot? Who knows?


Can we still get spare parts for this fused switch?


Thanks,


Z.


Parents
  • These devices are built like your proverbial brick dunny, so something major must have happened.


    Why not speak to Eaton? I have found them very helpful.


    I doubt that you will find the spare parts on fleabay and I'm not sure that I would want to buy second-hand.


    One last thing, have a close look at the fixed contacts and ensure that they have not been twisted.
Reply
  • These devices are built like your proverbial brick dunny, so something major must have happened.


    Why not speak to Eaton? I have found them very helpful.


    I doubt that you will find the spare parts on fleabay and I'm not sure that I would want to buy second-hand.


    One last thing, have a close look at the fixed contacts and ensure that they have not been twisted.