When connecting flexible wires using connection strip with screws it is recommended that one uses cord end sleeves or ferrules. What I realized if I connect two ferrules (1 In and 1 Out) the Insulation Jacket of ferules will not sufficiently enter the hole . and installation will end up as the attached figure. I am wondering if such connection is acceptable.
Note: in most cases I have 2x2.5mm2 Flex Wires In using Twin Ferrule and 1x2.5mm2 Flex wires out using single ferrule and I am using 10mm2 Connection strip
Another question is it acceptable to cut a little bit from the crimped ferrules so that they will enter sufficiently.
As long as the connection is inside an insulated enclosure or earthed metal enclosure then all should be o.k. There is not much metal showing and a British Standard finger can't gain access to a live part. Still, this connection should not be exposed to touch. I can't see anything wrong in reducing the finger length of a ferrule as long as the connection remains mechanically and electrically sound.
As long as the connection is inside an insulated enclosure or earthed metal enclosure then all should be o.k. There is not much metal showing and a British Standard finger can't gain access to a live part. Still, this connection should not be exposed to touch. I can't see anything wrong in reducing the finger length of a ferrule as long as the connection remains mechanically and electrically sound.