Good morning.

Would you classify the power supply from the main distribution panel to the lift as a sub main (5 sec disconnection time) or as a final circuit (0.4 sec disconnection time)?

The lift will take this power supply and ......if I am not wrong ..... distribute it further to lights and other automation components, so doesn't this mean that this is not a final circuit?

Thanks
Parents
  • Former Community Member
    0 Former Community Member
    OK - that looks like 411.3.2.2 (ii) then


    So 0.4 seconds on TN and 0.2 seconds if TT


    Regards


    OMS
Reply
  • Former Community Member
    0 Former Community Member
    OK - that looks like 411.3.2.2 (ii) then


    So 0.4 seconds on TN and 0.2 seconds if TT


    Regards


    OMS