Lift power supply disconnection time

Good morning.

Would you classify the power supply from the main distribution panel to the lift as a sub main (5 sec disconnection time) or as a final circuit (0.4 sec disconnection time)?

The lift will take this power supply and ......if I am not wrong ..... distribute it further to lights and other automation components, so doesn't this mean that this is not a final circuit?

Thanks
Parents
  • Or if all the loads downstream are protected, and really you are worried about it tripping when it should not, then lay in cable for a higher rated breaker. I'm assuming it is SWA or in conduit, so no RCD needed.
Reply
  • Or if all the loads downstream are protected, and really you are worried about it tripping when it should not, then lay in cable for a higher rated breaker. I'm assuming it is SWA or in conduit, so no RCD needed.