Lift power supply disconnection time

Good morning.

Would you classify the power supply from the main distribution panel to the lift as a sub main (5 sec disconnection time) or as a final circuit (0.4 sec disconnection time)?

The lift will take this power supply and ......if I am not wrong ..... distribute it further to lights and other automation components, so doesn't this mean that this is not a final circuit?

Thanks
Parents
  • Yes.

    It is 4c 4mm2 XLPE/SWA with 16A protection as per the lift manufacturer requirements.

    The lift manufacturer was asking for 2.5mm2 cable but it is 100m ride hence my problems.

    So it is 4mm2 now plus a separate earth.

    Cheers
Reply
  • Yes.

    It is 4c 4mm2 XLPE/SWA with 16A protection as per the lift manufacturer requirements.

    The lift manufacturer was asking for 2.5mm2 cable but it is 100m ride hence my problems.

    So it is 4mm2 now plus a separate earth.

    Cheers