This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

2-core SWA cabling

I’ve been doing some reading on the above, and some seem to suggest that the swa should not be relied upon for the CPC, what is the generally consensus on here, my thoughts are it appears to still be listed in the BBB, and in my opinion in certain conditions I.e. indoors so no risk of rust due to poor termination should be fine and if glanced correctly gives appropriate readings.
Parents
  • Benn22

    No problem using the swa as the cpc for a basic final or submain circuit. It gets more interesting when the cpc/swa has more than one function.

    Do the teachers at college still teach you to make off the glands correctly?


    Legh
Reply
  • Benn22

    No problem using the swa as the cpc for a basic final or submain circuit. It gets more interesting when the cpc/swa has more than one function.

    Do the teachers at college still teach you to make off the glands correctly?


    Legh
Children
No Data