Regulation 522.8.5 stating that its requirements for the support of cables and conductors are also applicable to consumer unit meter tails.

Regulation 522.8.5 stating that its requirements for the support of cables and conductors are also applicable to consumer unit meter tails.


So what types of clips are we to use, metal cleats?

Thoughts...


Regards

Simon
Parents

  • Notice the double socket ..




    Even if nothing is plugged in for normal use it is a good safe place to test earthing is present, L-N polarity is correct and a quick read of an upper limit for Zdb and a lower limit for PSSC for those situations that is required With the main switch off  using  a bit of cunning you can also do a whole site IR from there as well. Many countries recommend at least a single socket as part of the CU assembly for just this reason, along side an accessible earth terminal for wander lead R2 tests  - saves having to do the equivalent of  opening up  the Henley blocks. (and means you can plug in your clip lamp, drill, radio whatever, without trailing leads.)

    I'm in favour.

     


Reply

  • Notice the double socket ..




    Even if nothing is plugged in for normal use it is a good safe place to test earthing is present, L-N polarity is correct and a quick read of an upper limit for Zdb and a lower limit for PSSC for those situations that is required With the main switch off  using  a bit of cunning you can also do a whole site IR from there as well. Many countries recommend at least a single socket as part of the CU assembly for just this reason, along side an accessible earth terminal for wander lead R2 tests  - saves having to do the equivalent of  opening up  the Henley blocks. (and means you can plug in your clip lamp, drill, radio whatever, without trailing leads.)

    I'm in favour.

     