Rcbo white lead

Does anyone know the circuit arrangement for these loss of neutral protection leads?
Parents
  • The circuit is arranged with diodes to prevent any direct connection from N to E... there's a small chance of the diodes shorting I suppose, but the size of the FE wire would mean it would blow like a fuse before any substantial current could pass. It is much the same as say, on a DC supply, allowing a device to use either 4.5v from alkaline cells or 5.0v from usb, using diodes to prevent the 5v supply trying to charge the alkalines.
Reply
  • The circuit is arranged with diodes to prevent any direct connection from N to E... there's a small chance of the diodes shorting I suppose, but the size of the FE wire would mean it would blow like a fuse before any substantial current could pass. It is much the same as say, on a DC supply, allowing a device to use either 4.5v from alkaline cells or 5.0v from usb, using diodes to prevent the 5v supply trying to charge the alkalines.