Really unusual question.....

Does anyone know of any  FUSED  16A industrial IP67 plugs......   (blue plugs)


I have tried everywhere.......


really unusual use ... very long story  ......... but need to be fused
Parents

  • Harry Macdonald:

    Two short leads? One with 16A plug and 13A socket, the other with a 13A plug and a 16A socket. Put them in series if you really need the 16A plug on your stage equipment.

     



    But if anyone ever decides to connect a 16A load to the socket, you can be reasonably sure that the 13A fuse won't blow, but the plug may melt after a few hours.  It's a bit of a flaw in the design of the BS1363A plug.

     

Reply

  • Harry Macdonald:

    Two short leads? One with 16A plug and 13A socket, the other with a 13A plug and a 16A socket. Put them in series if you really need the 16A plug on your stage equipment.

     



    But if anyone ever decides to connect a 16A load to the socket, you can be reasonably sure that the 13A fuse won't blow, but the plug may melt after a few hours.  It's a bit of a flaw in the design of the BS1363A plug.

     