What`s this weeks quiz Zoom?
Parents
  • Not enough information...

    the original earth rod has been disconnected



     


    The supply is P.M.E.



    Is the installation utilizing the supplier's earth, or is the installation unearthed?


    Otherwise, plenty of C3s I imagine - no RCD additional protection to indoor sockets, lighting circuits, concealed cables and so on; probably no c.p.c. on lighting circuits, but provided there are no exposed-conductive-parts that's still only a C3 for me. Bathroom situation will need some careful looking at - but If it's all-copper pipework it'll probably satisfy the requirements for supplementary bonding between extraneous-conductive-parts and if there are no exposed-conductive-parts (typical batten lampholder with a HO skirt and a plastic pull switch setup) than I can't see anything beyond a C3 there either.


    A probable C is lack of RCD additional protection for portable equipment outdoors - so if there's a garden (and no RCD sockets marked 'for equipment outdoors' lurking somewhere) that would be a C2 for me and hence an unsatisfactory, but if there aren't any gardens, or perhaps just communal gardens that are maintained by contractors, maybe that's not a fail either.


    Size of tails will need checking (possibly against supplier's fuse - for that age anything down to 30A might be possible). If the tails really are unsheathed PVC (seems unlikely) then they might be a C2 - but accessibility needs to be taken into consideration - if they're within an enclosure that only gives access by means of a tool or key then they probably don't need a sheath to comply with the letter of the regs - it has even been suggested a meter box meets that requirement!


       - Andy.
Reply
  • Not enough information...

    the original earth rod has been disconnected



     


    The supply is P.M.E.



    Is the installation utilizing the supplier's earth, or is the installation unearthed?


    Otherwise, plenty of C3s I imagine - no RCD additional protection to indoor sockets, lighting circuits, concealed cables and so on; probably no c.p.c. on lighting circuits, but provided there are no exposed-conductive-parts that's still only a C3 for me. Bathroom situation will need some careful looking at - but If it's all-copper pipework it'll probably satisfy the requirements for supplementary bonding between extraneous-conductive-parts and if there are no exposed-conductive-parts (typical batten lampholder with a HO skirt and a plastic pull switch setup) than I can't see anything beyond a C3 there either.


    A probable C is lack of RCD additional protection for portable equipment outdoors - so if there's a garden (and no RCD sockets marked 'for equipment outdoors' lurking somewhere) that would be a C2 for me and hence an unsatisfactory, but if there aren't any gardens, or perhaps just communal gardens that are maintained by contractors, maybe that's not a fail either.


    Size of tails will need checking (possibly against supplier's fuse - for that age anything down to 30A might be possible). If the tails really are unsheathed PVC (seems unlikely) then they might be a C2 - but accessibility needs to be taken into consideration - if they're within an enclosure that only gives access by means of a tool or key then they probably don't need a sheath to comply with the letter of the regs - it has even been suggested a meter box meets that requirement!


       - Andy.