whjohnson:
This is an interesting one.
Last week I fitted 2 x WISKA plastic 1P65 8 way consumer units in garages and outbuildings.
WISKA state on the accompanying paperwork that their "......enclosures are manufactured and designed to be acceptable to take all the commercially available devices in line with BS EN 60898.
This complies with the R.D.842/2002, directive 2014/35/UE (DBT) and BSEN2208."
Make of that what you will.
I just fitted some stuff from CEF, namely a 30ma upfront main switch/RCD and a couple of mcbs.
OK, the switchgear was of one brand, but the enclosure was from another!
Alan Capon:
I would say it depends. If you are using Devices that have a higher breaking capacity than the supply PSSC, then C3. If the Devices have a lower breaking capacity than the supply PSSC, then you will be relying on the dispensation, and there could be justification for a C2.
Martynduerden:
But what about the enclosure itself Alan? Clearly the devices have a certified kA rating and that is fairly easy to ascertain but the enclosures kA rating is manufacturer certified subject to use of their prescribed devices . . .
John Peckham:
Martyn
The Regulation you are looking for is 536.4.203 for mix and match circuit breakers . A C3 unless the board has been mutilated, bus bars bent, cover cut away then a C2.