As an aside, What is the point in comparing to current regs and having C3 codes? The two things seem mutually exclusive, a C3 also seems an insurance risk, second guessing of the regulation it fails And deciding that one doesn't really matter if you like.
Cheers
Martyn
Alan Capon:
Martynduerden:
But what about the enclosure itself Alan? Clearly the devices have a certified kA rating and that is fairly easy to ascertain but the enclosures kA rating is manufacturer certified subject to use of their prescribed devices . . .That is where the entertainment begins. In theory an mcb used at or below its rated fault current will trip on a fault as everyone expects every time. If the mcb is used above it’s rated current, it may trip correctly, or it may fail catastrophically. The idea of the conditional “rated assembly” is that if the device fails attempting to trip, the enclosure will contain all the bits, including the explosion until the upstream protective device (the supplier’s cutout for example) clears the fault. If the type-tested assembly fails, then the manufacturer may be liable. If they can then prove the presence of another manufacturer’s device or a device of theirs that was not included in the testing was fitted, then it is likely they have no liability.
My reason for not giving a definite response, is that a catastrophic failure of a type-tested assembly would have to be examined in a court of law for an absolute judgement.
Regards,
Alan.
John Peckham:
Martyn
The Regulation you are looking for is 536.4.203 for mix and match circuit breakers . A C3 unless the board has been mutilated, bus bars bent, cover cut away then a C2.
We're about to take you to the IET registration website. Don't worry though, you'll be sent straight back to the community after completing the registration.
Continue to the IET registration site