Coding muddled circuits

This isn't quite what happened ...


You are doing a PIR on a property which has had about three phases of alterations. The householder wants to retain power so that she may use Wifi for her work, so each circuit is locked off individually. Whilst inspecting the downstairs lights, you undo a switch which controls an outdoor luminaire beside a door leading from the dining room to the garden. You get a shock (both literally and figuratively). ?


FI reveals that the lamp was fed from the upstairs lighting circuit.


I think that such a situation is rather dangerous. One might argue that safe isolation should be applied to every accessory, but I think that it would be reasonable for an ordinary person to change a broken switch. It isn't so much a matter of one fault to danger, but one repair to danger.


It also means that if the CU is marked "downstairs lights" and "upstairs lights", the markings are inappropriate.


C2 seems rather extreme - a lot of effort might be required to separate the circuits.

C3 gets my vote.

no code seems reasonable subject to the installation being sound in all other respects.


Interested to hear your views!
Parents
  • Sort to say it Chris, but it is not worthy of a code on an EICR and you got a shock because you did not follow the correct method of work.


    I have done it myself, I went to change a PIR operated outside light and flicked all the lighting circuit MCBs off and the switch inside the entrance door, however the light was connected to a socket circuit with a fused connection unit tucked away in a cupboard. Another time I turned a kitchen light off at the MCB in the CU which was in the same room and saw it go out, so I jumped up on the hop up to start work and found out the hard way that the ceiling rose was connected to two circuits.


    One day we might not get away with it, so keep testing.


    Andy Betteridge
Reply
  • Sort to say it Chris, but it is not worthy of a code on an EICR and you got a shock because you did not follow the correct method of work.


    I have done it myself, I went to change a PIR operated outside light and flicked all the lighting circuit MCBs off and the switch inside the entrance door, however the light was connected to a socket circuit with a fused connection unit tucked away in a cupboard. Another time I turned a kitchen light off at the MCB in the CU which was in the same room and saw it go out, so I jumped up on the hop up to start work and found out the hard way that the ceiling rose was connected to two circuits.


    One day we might not get away with it, so keep testing.


    Andy Betteridge