Coding muddled circuits

This isn't quite what happened ...


You are doing a PIR on a property which has had about three phases of alterations. The householder wants to retain power so that she may use Wifi for her work, so each circuit is locked off individually. Whilst inspecting the downstairs lights, you undo a switch which controls an outdoor luminaire beside a door leading from the dining room to the garden. You get a shock (both literally and figuratively). ?


FI reveals that the lamp was fed from the upstairs lighting circuit.


I think that such a situation is rather dangerous. One might argue that safe isolation should be applied to every accessory, but I think that it would be reasonable for an ordinary person to change a broken switch. It isn't so much a matter of one fault to danger, but one repair to danger.


It also means that if the CU is marked "downstairs lights" and "upstairs lights", the markings are inappropriate.


C2 seems rather extreme - a lot of effort might be required to separate the circuits.

C3 gets my vote.

no code seems reasonable subject to the installation being sound in all other respects.


Interested to hear your views!
Parents

  • ebee:




    Sparkingchip:
    063cd132030b0728d101d3e502d05383-huge-20200211_110124.jpg

    One from this morning. 

    Andy B. 




    Reminds a bit of that old chestnut. Two rings, one leg of each ring into one fuseway and the other leg of each ring into another fuseway. Quite entertaining and a good prove dead example


     




    Unsurprisingly the issue involved the 32 amp MCB to the right hand side,the two conductors that had continuity ended up in the 32 and the rest in the 16. I only wanted to connect the new brown conductors that’s in the top of the picture.


    Andy 

Reply

  • ebee:




    Sparkingchip:
    063cd132030b0728d101d3e502d05383-huge-20200211_110124.jpg

    One from this morning. 

    Andy B. 




    Reminds a bit of that old chestnut. Two rings, one leg of each ring into one fuseway and the other leg of each ring into another fuseway. Quite entertaining and a good prove dead example


     




    Unsurprisingly the issue involved the 32 amp MCB to the right hand side,the two conductors that had continuity ended up in the 32 and the rest in the 16. I only wanted to connect the new brown conductors that’s in the top of the picture.


    Andy 