Legh Richardson:
The cloth, and rubber appears to be in reasonable condition for what appears to be nearly 70 years old. An insulation test at 500V gave a reasonable result (>500M) and a leakage test gave the same, 0.41mA.
The cable is out of date but appears to be still serviceable. It is not heavily used and the ambient temperature is generally quite low. I think I might advise that the cable is replaced by a newer edition or at least regularly checked every year. Has anybody got any other ideas?
Legh Richardson:
The cloth, and rubber appears to be in reasonable condition for what appears to be nearly 70 years old. An insulation test at 500V gave a reasonable result (>500M) and a leakage test gave the same, 0.41mA.
The cable is out of date but appears to be still serviceable. It is not heavily used and the ambient temperature is generally quite low. I think I might advise that the cable is replaced by a newer edition or at least regularly checked every year. Has anybody got any other ideas?