This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

rubber insulated cloth covered tinned copper submain cable in galv. conduit.

Had a look at an installation which has a submain running approximately 25m to supply a kitchen.

We thought umm this looks interesting, cut a slice off at the output of the switched fuse and re-terminated. The cloth, and rubber appears to be in reasonable condition for what appears to be nearly 70 years old. An insulation test at 500V gave a reasonable result (>500M) and a leakage test gave the same, 0.41mA.

The cable is out of date but appears to be still serviceable. It is not heavily used and the ambient temperature is generally quite low. I think I might advise that the cable is replaced by a newer edition or at least regularly checked every year. Has anybody got any other ideas?


Legh
Parents

  • MHRestorations:

    I noted the same with the TRS cable in our house. sharpened tile bits for tiles



    TRS is Tough Rubber Sheathed cable and not the same as Vulcanised Rubber Insulated cable.


    Jaymack
Reply

  • MHRestorations:

    I noted the same with the TRS cable in our house. sharpened tile bits for tiles



    TRS is Tough Rubber Sheathed cable and not the same as Vulcanised Rubber Insulated cable.


    Jaymack
Children
No Data