132.16 states: "No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measures applied for safety of the installation, shall be adequate."
AJJewsbury:
132.16 states: "No addition or alteration, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measures applied for safety of the installation, shall be adequate."
My copy seems to have slightly different wording...
No addition, temporary or permanent, shall be made to an existing installation, unless it has been ascertained that the rating and the condition of any existing equipment, including that of the distributor, will be adequate for the altered circumstances. Furthermore, the earthing and bonding arrangements, if necessary for the protective measure applied for the safety of the alteration or addition, shall be adequate.
I don't know if that helps any...
- Andy.
Chris Pearson:
No, it doesn't mean that.
My interpretation is that all parts of the installation upstream of the alteration or addition, and the earthing and bonding so far as they affect safety of the alteration or addition, must be adequate.
The paragraph does not apply to any other existing parts of the installation.
644.1.2 prohibits the issuing of an EIC until any relevant defects have been remedied. Other defects may be mentioned in the "comments on existing installation" part of an EIC or MWC.
A new CU does not adversely affect the safety of existing circuits, but the earthing and bonding must be brought up to the appropriate standard to ensure that the CU is safe.