This discussion has been locked.
You can no longer post new replies to this discussion. If you have a question you can start a new discussion

Details of BS7671:2018 Amendment 1 are here.

Details of Amendment 1 of BS7671:2018 is available here: https://electrical.theiet.org/bs-7671/updates/


Regards,


Alan.
Parents

  • AJJewsbury:




    Paul Judd:

    Is the formula for calculating the maximum neutral current (Im) in Annex A722; A722.1 Neutral current of a three-phase installation, actually correct?


    There's an L missing (IL3) and only half of the final multiplication is shown. 


    Probably!

     




    Good question - it's also nothing like the formula in BS 7671:2018 yet doesn't have any change bars...


      - Andy.


     




    The correct expression is:

    bea1b3f366016bc756977985ec71ea38-huge-a722.1.jpg


    Mathematically, it is identical to the expression in BS 7671:2018 ... if you consider that 0.866 = SQRT(3)/2 and do a bit of algebra.


    The replacement is more likely to have been encountered by those who have come across three-phase calculations in text books.

Reply

  • AJJewsbury:




    Paul Judd:

    Is the formula for calculating the maximum neutral current (Im) in Annex A722; A722.1 Neutral current of a three-phase installation, actually correct?


    There's an L missing (IL3) and only half of the final multiplication is shown. 


    Probably!

     




    Good question - it's also nothing like the formula in BS 7671:2018 yet doesn't have any change bars...


      - Andy.


     




    The correct expression is:

    bea1b3f366016bc756977985ec71ea38-huge-a722.1.jpg


    Mathematically, it is identical to the expression in BS 7671:2018 ... if you consider that 0.866 = SQRT(3)/2 and do a bit of algebra.


    The replacement is more likely to have been encountered by those who have come across three-phase calculations in text books.

Children
No Data