This discussion is locked.
You cannot post a reply to this discussion. If you have a question start a new discussion

Neutral Earth connection

Former Community Member
Former Community Member
Interrogating an issue with a substation set up - The substation is a split one with two 11Kv to 400v cast resin transformers that supply each substation half. The set up incorporates back up generators that kick in on a power cut, I noticed that we have a UPS system installed that takes two supplies from the substation, one from each half. either one is on and the other supply stays as backup to the UPS system. What was picked up is that when there is a power cut and until the power is restored there is a load shed that disconnects the supply to the UPS. This UPS remains on feeding 400v three phase to the site, but the earth neutral connection is lost until one of the supply breakers closes back up again. means that the output is not referenced to earth for a few minutes till the gens spin up. I believe that through checking manuals and reading up this isnt a good scenario to be in in terms of sensitive equipment. 


I would be looking at providing a transformer in there along with a local earth neutral link so that this is maintained on all eventualities. has anyone come up with this sort of issue before ? it could also be addressed through neutral earth contactors at the appropriate places, Had looked at possible three pole devices on circuit breakers but that does not allow full isolation to be achieved and could also lead to possible paralleling of the neutral earth link at each transformer.
Parents
  • Former Community Member
    0 Former Community Member
    Thanks


    Issue is the generation is 11Kv, two transformers provide 400v 3Ph on a TN-S, neutral link is at transformer and there are four pole devices on supply breaker. 4 pole devices on the UPS supplies awell. Checked it out and the UPS def runs sans neutral earth link during swaps from utility to generator
Reply
  • Former Community Member
    0 Former Community Member
    Thanks


    Issue is the generation is 11Kv, two transformers provide 400v 3Ph on a TN-S, neutral link is at transformer and there are four pole devices on supply breaker. 4 pole devices on the UPS supplies awell. Checked it out and the UPS def runs sans neutral earth link during swaps from utility to generator
Children
No Data