Earthing/Bonding advise please

Hi all, i'm after some advise and thought this would be the best place to ask ?


I have a supply cable to an out building, currently in 16mm T&E and an underground copper water supply also in the out building.  The pipe currently has no bonding.

I want to upgrade the cable to the out building.  Would a 16mm 3 core SWA be suitable, using the 3rd core as a combined CPC and bonding conductor.


Main supply to house is overhead assumed to be TNS due to the supply cable being Split Concentric....



Thanks in advance
Parents
  • Thanks for you time Andy, much appreciated.


    The old T&E is unsightly as it runs around the middle of the house, I am clipping the SWA around the bottom of the house and a short underground run (about 1.5 meters) under some flags to the out building.  Also the cable was selected with a good safety margin.

    I'll stick with this idea as I have the materials and not a fan of TT.

    Not an option to replace pipe for plastic as it comes in under a concrete floor.

    Is it common to find unbonded extraneous conductors? 


    Another question, what size should the links be from the SWA glands to the earth terminal?


    Thanks again.
Reply
  • Thanks for you time Andy, much appreciated.


    The old T&E is unsightly as it runs around the middle of the house, I am clipping the SWA around the bottom of the house and a short underground run (about 1.5 meters) under some flags to the out building.  Also the cable was selected with a good safety margin.

    I'll stick with this idea as I have the materials and not a fan of TT.

    Not an option to replace pipe for plastic as it comes in under a concrete floor.

    Is it common to find unbonded extraneous conductors? 


    Another question, what size should the links be from the SWA glands to the earth terminal?


    Thanks again.