RCD socket outlet.

Former Community Member
Former Community Member
Hi all,
Any comments on this one most welcome!
A customer wants me to replace an existing one gang 13 amp socket outlet with a double.
The problem is that there's no rcd protection there, so i'm thinking that as I am in effect adding a socket outlet I should fit an rcd protected one?
If I were replacing like for like it wouldn't bother me at all but the fact it's going to be a double makes me think an rcd protected one is the thing to do, just seems a bit ott to fit one rcd protected socket when there are probably 20 others that aren't rcd'd!
Parents
  • Andy


    Thanks for the cue? Sockets with an integral RCD to BS7288 are not regognised in BS 7671, in fact they are excluded as BS 7671 only permis 3 devices for Additional Protection for use by ordinary persons.


    SRCD sockets and FCU to BS 7288 can only be used where they have upstream RCD protection. I know that sparkles may think that is daft, wish it were not true or may disagree with me. If so I would commend they read BS 7288: 2016.


    i would suggest Dave you fit an RCBO in the board, if it will not take one then fit an external RCD in an enclosure next to the board.
Reply
  • Andy


    Thanks for the cue? Sockets with an integral RCD to BS7288 are not regognised in BS 7671, in fact they are excluded as BS 7671 only permis 3 devices for Additional Protection for use by ordinary persons.


    SRCD sockets and FCU to BS 7288 can only be used where they have upstream RCD protection. I know that sparkles may think that is daft, wish it were not true or may disagree with me. If so I would commend they read BS 7288: 2016.


    i would suggest Dave you fit an RCBO in the board, if it will not take one then fit an external RCD in an enclosure next to the board.