John Peckham:
Andy
Thanks for the cue? Sockets with an integral RCD to BS7288 are not regognised in BS 7671, in fact they are excluded as BS 7671 only permis 3 devices for Additional Protection for use by ordinary persons.
SRCD sockets and FCU to BS 7288 can only be used where they have upstream RCD protection. I know that sparkles may think that is daft, wish it were not true or may disagree with me. If so I would commend they read BS 7288: 2016.
i would suggest Dave you fit an RCBO in the board, if it will not take one then fit an external RCD in an enclosure next to the board.
John Peckham:
Andy
Thanks for the cue? Sockets with an integral RCD to BS7288 are not regognised in BS 7671, in fact they are excluded as BS 7671 only permis 3 devices for Additional Protection for use by ordinary persons.
SRCD sockets and FCU to BS 7288 can only be used where they have upstream RCD protection. I know that sparkles may think that is daft, wish it were not true or may disagree with me. If so I would commend they read BS 7288: 2016.
i would suggest Dave you fit an RCBO in the board, if it will not take one then fit an external RCD in an enclosure next to the board.