RCD socket outlet.

Former Community Member
Former Community Member
Hi all,
Any comments on this one most welcome!
A customer wants me to replace an existing one gang 13 amp socket outlet with a double.
The problem is that there's no rcd protection there, so i'm thinking that as I am in effect adding a socket outlet I should fit an rcd protected one?
If I were replacing like for like it wouldn't bother me at all but the fact it's going to be a double makes me think an rcd protected one is the thing to do, just seems a bit ott to fit one rcd protected socket when there are probably 20 others that aren't rcd'd!
Parents
  • The law only requires you not to make an installation any more dangerous than it already was.

    There is no need to bring it fully to current standards if it is unreasonable to do so.

    If you belong to NICIEC, their house rules may suggest otherwise, but that is not law.
Reply
  • The law only requires you not to make an installation any more dangerous than it already was.

    There is no need to bring it fully to current standards if it is unreasonable to do so.

    If you belong to NICIEC, their house rules may suggest otherwise, but that is not law.