RCD socket outlet.

Former Community Member
Former Community Member
Hi all,
Any comments on this one most welcome!
A customer wants me to replace an existing one gang 13 amp socket outlet with a double.
The problem is that there's no rcd protection there, so i'm thinking that as I am in effect adding a socket outlet I should fit an rcd protected one?
If I were replacing like for like it wouldn't bother me at all but the fact it's going to be a double makes me think an rcd protected one is the thing to do, just seems a bit ott to fit one rcd protected socket when there are probably 20 others that aren't rcd'd!
Parents
  • A socket outlet or SCFU with a built in RCD will only provide RCD protection to what is connected downstream of if.


    So for example if the main earth conductor is missing or defective a fault on an existing non-RCD protected circuit elsewhere in the installation such as a lighting circuit could raise the touch voltage on the metal case of an appliance downstream of the RCD socket or SFCU to a dangerous level.


    Now for the REALITY CHECK there is EXACTLY THE SAME RISK if the circuit has a RCD or RCBO upfront of it in or alongside the consumer unit.


    So any 30 mA RCD device can only be installed with confidence if the circuit and equipment downstream of it it effectively earthed so that a fault elsewhere in the installation won’t raise the voltage on the CPC and connected class I appliances above 50 volts and in a TT installation there is a suitably rated and effective RCD main switch.


    Do not forget the basic requirements for safe electrical installation work.


     Andy Betteridge 


Reply
  • A socket outlet or SCFU with a built in RCD will only provide RCD protection to what is connected downstream of if.


    So for example if the main earth conductor is missing or defective a fault on an existing non-RCD protected circuit elsewhere in the installation such as a lighting circuit could raise the touch voltage on the metal case of an appliance downstream of the RCD socket or SFCU to a dangerous level.


    Now for the REALITY CHECK there is EXACTLY THE SAME RISK if the circuit has a RCD or RCBO upfront of it in or alongside the consumer unit.


    So any 30 mA RCD device can only be installed with confidence if the circuit and equipment downstream of it it effectively earthed so that a fault elsewhere in the installation won’t raise the voltage on the CPC and connected class I appliances above 50 volts and in a TT installation there is a suitably rated and effective RCD main switch.


    Do not forget the basic requirements for safe electrical installation work.


     Andy Betteridge 