RCD socket outlet.

Former Community Member
Former Community Member
Hi all,
Any comments on this one most welcome!
A customer wants me to replace an existing one gang 13 amp socket outlet with a double.
The problem is that there's no rcd protection there, so i'm thinking that as I am in effect adding a socket outlet I should fit an rcd protected one?
If I were replacing like for like it wouldn't bother me at all but the fact it's going to be a double makes me think an rcd protected one is the thing to do, just seems a bit ott to fit one rcd protected socket when there are probably 20 others that aren't rcd'd!
Parents
  • I am sat trying to do an invoice that I should have done a few weeks ago, there have been a series of very brief power outages on the local power supply that has knocked my desktop computer off at least ten times now as well as taking down the home internet connection, I’m losing the will to carry on trying to do the invoice at the moment.


    Regards the installation of SRCD devices, they were only a choice of last resort when a DP RCD could not be sensibly installed.


    So moving on I have actually bought a supply of Europa double pole RCBOs  and enclosures, now explain me how one of those inserted into an existing circuit affords a better level of additional protection than a DP SRCD?
Reply
  • I am sat trying to do an invoice that I should have done a few weeks ago, there have been a series of very brief power outages on the local power supply that has knocked my desktop computer off at least ten times now as well as taking down the home internet connection, I’m losing the will to carry on trying to do the invoice at the moment.


    Regards the installation of SRCD devices, they were only a choice of last resort when a DP RCD could not be sensibly installed.


    So moving on I have actually bought a supply of Europa double pole RCBOs  and enclosures, now explain me how one of those inserted into an existing circuit affords a better level of additional protection than a DP SRCD?