RCD socket outlet.

Former Community Member
Former Community Member
Hi all,
Any comments on this one most welcome!
A customer wants me to replace an existing one gang 13 amp socket outlet with a double.
The problem is that there's no rcd protection there, so i'm thinking that as I am in effect adding a socket outlet I should fit an rcd protected one?
If I were replacing like for like it wouldn't bother me at all but the fact it's going to be a double makes me think an rcd protected one is the thing to do, just seems a bit ott to fit one rcd protected socket when there are probably 20 others that aren't rcd'd!
Parents
  • The point is there are installations with earthing and bonding that were installed and considered safe, the requirement that has come in requires ADDITIONAL protection in some locations using 30 mA RCDs, that does not actually mean the original requirement has been removed, it is additional not instead of.


    You cannot insert a RCD into a dangerous circuit and say that you have done a good job, it has to meet all the basic requirements.


    Andy Betteridge
Reply
  • The point is there are installations with earthing and bonding that were installed and considered safe, the requirement that has come in requires ADDITIONAL protection in some locations using 30 mA RCDs, that does not actually mean the original requirement has been removed, it is additional not instead of.


    You cannot insert a RCD into a dangerous circuit and say that you have done a good job, it has to meet all the basic requirements.