John Peckham:
Chris
Your SRCD near doors to the outside on your 15th Edition installation were no no doubt put there to comply with regulation 471-12 of the 15th Edition to protect leads and appliances going outside the equipotential zone. Your SRCDs would have no doubt complied with BS 7288-1990 not the current BS 7288-2016. I would recommend you bring your whole installation up to the 18th Edition standard for the added benefits. Just to show I am not smug I have a house with a 16th Edition installation. I have a new dual RCD board sitting on the floor waiting for me to get my a**e in to gear and get it fitted, in my defence I do now have Type 2 surge protection on my newly fitted REC 2 isolator carried out as part of the enabling works for the CU upgrade.
If I may ask a rude question, " Are you happy to sign EICs and Minor Works as being compliant with BS 7671 when you have fitted an SRCD"? How would you code a BS 7288-2016 having discovered one on a periodic inspection?
John Peckham:
Good morning members of the flat earth society, at least it feels that way as those people refuse to believed any evidence that is contrary to their belief.
A few points that may help some of you come to a different view.
4.BS 7671 511.1. and then a look through Appendix 1 to see if BS 7288 is there?
5. BS 7671 Regulation 133.1.3.
John Peckham:
"So moving on I have actually bought a supply of Europa double pole RCBOs and enclosures, now explain me how one of those inserted into an existing circuit affords a better level of additional protection than a DP SRCD?"
Because they comply with BS EN 61008 which is a device tested to a higher standard than BS 7288 devices and they comply with the requirement set out in 531.3.4.1. I feel sure you will soon see an SRCD that complies with BS EN 61008, BS 1363 and BS 7288.
weirdbeard:
Hi John, BS 7288 wasn't listed in appendix 1 of the 2008 17th edition, and here is a related topic from ye old forum:
https://www2.theiet.org/forums/forum/messageview.cfm?catid=205&threadid=28346
Would you mind explaining why this has fairly recently become an issue that you hold dearly? ps, you seem to be struggling to get your new board fitted, I have a couple of hours spare next week if you need any help :)
John Peckham:
Andy
Wrong about the fault current rating by a long way.