John Peckham:
Andy
Wrong about the fault current rating by a long way.
jcm:
Reading this thread is the HSE not keeping up with the current regulations, thinking about electrical recommends for HP Washers and stm HP HW cleaners . A 13 amp socket with a built in RCD can form part of a fixed installation , but the number of these sockets I found seized (larger wattage power washers) ,can't pull put the plug top due to burnt pins , I was always careful to recommend or demand replace with a 16amp RCD outlet. The HSE leaflet
below:
www.hse.gov.uk/.../pm29.pdf
jcm
UKPN:
So I am in the clear using a masterplug RCD adaptor in a socket outlet? To quote the manufacturer " ideally you would use an RCD adaptor with any electrical appliance"
For those suffering with BS paranoia, the number is = 7071 1992.
Regards, UKPN
Sparkingchip:
UKPN:
So I am in the clear using a masterplug RCD adaptor in a socket outlet? To quote the manufacturer " ideally you would use an RCD adaptor with any electrical appliance"
For those suffering with BS paranoia, the number is = 7071 1992.
Regards, UKPN
Is your earthing and bonding in place?
Actually most garden power tools like mowers are now double insulated so getting a shock off a faulty electric heater in a bedroom whilst mowing the lawn in the garden is not going to be a problem.
That is exactly the point I was making, you cannot connect a RCD to a circuit and installation that is not adequately earthed and bonded or else a fault elsewhere in the installation may raise the voltage of earthed equipment downstream of the RCD to dangerous levels, a RCD does not remove the requirements for basic and fault protection along with the requirement to mitigate touch voltages.
AJJewsbury:
That is exactly the point I was making, you cannot connect a RCD to a circuit and installation that is not adequately earthed and bonded or else a fault elsewhere in the installation may raise the voltage of earthed equipment downstream of the RCD to dangerous levels, a RCD does not remove the requirements for basic and fault protection along with the requirement to mitigate touch voltages.
The point I was attempting to make was than even in a fully correctly earthed & bonded installation a fault elsewhere can raise the exposed-conductive-parts downstream of the RCD (as elsewhere) to dangerous levels - e.g. >115V for 5s in a TN system or 230V for 1s in a TT system - the 'mixed disconnection time problem' isn't just something for inadequately earthed/bonded installations to worry about.
There is some advantage in having all your RCDs close to the MET (with the minimum of parallel paths on the c.p.c.s) - in that faults on your circuit are covered by the rapid disconnection time of your RCD and faults on other circuits shouldn't raise the potential on your c.p.c. relative to the MET (where both your c.p.c. and main bonding are connected) - but BS 7671 doesn't clearly advocate that approach (although perhaps hints at it in section 701).
- Andy.