Non-Conducting Location.

To reduce costs I am considering creating a non-conducting location in a wooden holiday chalet.


The maintenance of the wooden building will be by skilled and instructed persons only.


The chalet is wooden framed and has wooden external ship lap with a water proof membrane in between the outside ship lap and inner plasterboard. . The roof is glass fibre. The wooden floor is supported on wooden joists on a concrete base. The flooring will be vinyl coverings. All window frames are plastic.


The main water supply pipe is plastic. There is no gas supply at all either mains or bottled gas. 


There are no extraneous-conductive -parts.


No outside equipment will be used.


All wiring accessories will be all insulated.


Appliances can be separated by at least 2.5m distance.


Can I safely apply 418.1.3?


Thanks,


Z.








Parents
  • If it is a holiday chalet, and still being used as such by the general public, then, no. Your idea of 'closely controlled' access is not the same as will be expected. Warning signs, door interlocks, permits and tokens, training of all persons using the facility before entry is granted.


    If it is an ex holiday chalet being repurposed to become a chamber for housing specialist high voltage  kit, then maybe.


    The principle is that the voltage reached by any exposed metalwork is not a hazard because it is not possible to touch two pieces of metalwork with differing voltage levels at the same time. Care must be taken, however, to make sure that a dangerous  potential cannot be transmitted outside the location by the subsequent installation of a conductor such as a cable, a pipe or structural metalwork, indeed anything that penetrates the insulating enclosure.


    Consider, if two faults to near exposed conductive parts occur from conductors at different potentials (such as a phase and a neutral or two phases ) dangerous potential differences could occur between exposed conductive parts, nothing will trip.


    Double pole fuses or double pole breaking circuit breakers are used for ADS protection in non-conducting locations as the idea of neutral being safer than live is lost, the user is as likely to be at live potential as any other.


    I would not expect to see any kind of 3 pin sockets or any kind of metal light fitting requiring a CPC, if out of reach or not.


    A notice must be erected to state that the non-conducting location exists, and giving details of the person in charge (supervising) who alone has authority to authorize access to the facility and any experiment or testing  to be undertaken within, and to be responsible for what equipment may be used in the location.

    I'd expect records of training to be signed by the users and kept by the supervisor, along with results of inspections and a list of authorized equipment. All such records to be maintained in a condition available for inspection by the authorities as an audit trail in case of incident.


    Non-conducting locations are rarely the best solution to the safety problem and so are most unusual, and their use must be limited to situations where there is continuous and proper supervision to ensure that the safety requirements are fully met and are properly maintained, and in my personal view they should be restricted to situations where no more reliable system of ensuring safety is possible.
Reply
  • If it is a holiday chalet, and still being used as such by the general public, then, no. Your idea of 'closely controlled' access is not the same as will be expected. Warning signs, door interlocks, permits and tokens, training of all persons using the facility before entry is granted.


    If it is an ex holiday chalet being repurposed to become a chamber for housing specialist high voltage  kit, then maybe.


    The principle is that the voltage reached by any exposed metalwork is not a hazard because it is not possible to touch two pieces of metalwork with differing voltage levels at the same time. Care must be taken, however, to make sure that a dangerous  potential cannot be transmitted outside the location by the subsequent installation of a conductor such as a cable, a pipe or structural metalwork, indeed anything that penetrates the insulating enclosure.


    Consider, if two faults to near exposed conductive parts occur from conductors at different potentials (such as a phase and a neutral or two phases ) dangerous potential differences could occur between exposed conductive parts, nothing will trip.


    Double pole fuses or double pole breaking circuit breakers are used for ADS protection in non-conducting locations as the idea of neutral being safer than live is lost, the user is as likely to be at live potential as any other.


    I would not expect to see any kind of 3 pin sockets or any kind of metal light fitting requiring a CPC, if out of reach or not.


    A notice must be erected to state that the non-conducting location exists, and giving details of the person in charge (supervising) who alone has authority to authorize access to the facility and any experiment or testing  to be undertaken within, and to be responsible for what equipment may be used in the location.

    I'd expect records of training to be signed by the users and kept by the supervisor, along with results of inspections and a list of authorized equipment. All such records to be maintained in a condition available for inspection by the authorities as an audit trail in case of incident.


    Non-conducting locations are rarely the best solution to the safety problem and so are most unusual, and their use must be limited to situations where there is continuous and proper supervision to ensure that the safety requirements are fully met and are properly maintained, and in my personal view they should be restricted to situations where no more reliable system of ensuring safety is possible.