AJJewsbury:
Just for information, there was a case a while ago where a shaver socket had been used to re-charge an electric toothbrush but the transformer had overheated despite the toothbrush charger drawing less current than a typical shaver. The socket manufacturer's defence was that the device was clearly marked 'shavers only' and it was the long-duration nature of the load that had caused the issue - the nominal shaver socket VA rating being only valid for the short duration typically needed for a shave. I suppose that's similar to the 'tool rating' of CTE site transformers - the continuous rating being far lower.
AJJewsbury:
Just for information, there was a case a while ago where a shaver socket had been used to re-charge an electric toothbrush but the transformer had overheated despite the toothbrush charger drawing less current than a typical shaver. The socket manufacturer's defence was that the device was clearly marked 'shavers only' and it was the long-duration nature of the load that had caused the issue - the nominal shaver socket VA rating being only valid for the short duration typically needed for a shave. I suppose that's similar to the 'tool rating' of CTE site transformers - the continuous rating being far lower.