I have to replace 6 pitch boxes on a touring van caravan  site.

So six pitch boxes with 4 van hookup points per box, each hookup point protected by a 10A 30mA RCCB.

Unfortunately I've also discovered that the site is wired as a ring in 6mm SWA, buried direct in ground.


Any thoughts on max fuse size to protect a 6mm ring?


Regards

George
Parents
  • Former Community Member
    0 Former Community Member
    There may be concerns already by the provision of 10 A devices for each of the 24 pitches. Was was the original device rating? A nail? 


    Even if you were to use a 73 A device, you're looking at just 3 A per pitch..................


    Regards


    BOD
Reply
  • Former Community Member
    0 Former Community Member
    There may be concerns already by the provision of 10 A devices for each of the 24 pitches. Was was the original device rating? A nail? 


    Even if you were to use a 73 A device, you're looking at just 3 A per pitch..................


    Regards


    BOD